Lab 1: West Data Center Configuration
In this lab you will be configuring a BIG-IP HA cluster and setting it to advertise available virtual servers through the BGP protocol.
Configure the BIG-IP HA Cluster in the West Data Center
From the jumphost ssh to the W_A_BIGIP-13
root@jumphost:~# ssh -l root 192.168.1.3
tmsh modify sys ntp servers add { pool.ntp.org }
tmsh mv cm device bigip1 W_A_BIGIP-13.local
tmsh modify cm device W_A_BIGIP-13.local configsync-ip 192.168.255.10
tmsh modify cm device W_A_BIGIP-13.local  unicast-address { { ip 192.168.255.10 } }
From the jumphost ssh to the W_B_BIGIP-13
root@jumphost:~# ssh -l root 192.168.1.6
tmsh mv cm device bigip1 W_B_BIGIP-13.local
tmsh modify cm device W_B_BIGIP-13.local configsync-ip 192.168.255.11
tmsh modify cm device W_B_BIGIP-13.local  unicast-address { { ip 192.168.255.11 } }
Create the trust domain and sync-failover group from one of the two BIGIP's:
From W_B_BIGIP-13
tmsh modify cm trust-domain /Common/Root ca-devices add { 192.168.255.10 } name W_A_BIGIP-13.local username admin password admin
tmsh create cm device-group sync-failover type sync-failover auto-sync enabled save-on-auto-sync true devices add { W_A_BIGIP-13.local W_B_BIGIP-13.local }
Run the initial configuration sync from one of the two BIGIP's:
tmsh run cm config-sync to-group sync-failover
[root@W_B_BIGIP-13:Active:Changes Pending] config #
[root@W_B_BIGIP-13:Active:Awaiting Initial Sync] config #
[root@W_B_BIGIP-13:Active:In Sync] config #
Save the configuration on both BIG-IP devices
tmsh save sys config partitions all
Create an application configuration for a virtual server and a pool member
Create the following virtual server and pool member
tmsh create ltm pool pool1 members add { 10.3.99.200:80 } monitor tcp_half_open
tmsh create ltm virtual vip1 destination 10.99.99.100:80 source-address-translation { type automap } pool pool1 profiles add { tcp http }
Note
The configuration should now be auto-sync'd to the other device and auto-saved.
Attention
The virtual server is not available.
[root@W_A_BIGIP-13:Standby:In Sync] config # tmsh show ltm virtual
Ltm::Virtual Server: vip1
Status
  Availability     : offline
  State            : enabled
  Reason           : The children pool member(s) are down
  CMP              : enabled
  CMP Mode         : all-cpus
  Destination      : 10.99.99.100:80
The pool members are unavailable.
[root@W_A_BIGIP-13:Standby:In Sync] config # tmsh show ltm pool
Ltm::Pool: pool1
Status
  State        : enabled
  Monitor      : tcp_half_open
  Minimum Active Members : 0
  Current Active Members : 0
       Available Members : 0
           Total Members : 1
          Total Requests : 0
        Current Sessions : 0
You need to create a static route to the web server located in the core network on both BIG-IPs.
tmsh create net route webservers network 10.3.99.0/24 gw 10.1.20.254
Note
This only needs to be configured on one device as seen below
[root@W_B_BIGIP-13:Active:In Sync] config # tmsh create net route webservers network 10.3.99.0/24 gw 10.1.20.254
[root@W_B_BIGIP-13:Active:Not All Devices Synced] config #
Your virtual server should now show available.
Status
  Availability     : available
  State            : enabled
  Reason           : The virtual server is available
  CMP              : enabled
  CMP Mode         : all-cpus
Note
From the jump host you can now try to reach the website
Either open a web browser and browse to http://10.99.99.100 or from the jump host CLI, type:
curl http://10.99.99.100
Why is it not available?
Configure the route advertisement on the BIG-IP cluster
On both W_A_BIGIP and W_B_BIGIP configure the following:
tmsh modify net route-domain 0 routing-protocol add { BGP }
Note
The following just needs to be applied on just one device
tmsh modify ltm virtual-address 10.99.99.100 route-advertisement all
Note
route-advertisement
Specifies the route advertisement setting for the virtual address. The default value is disabled.
enabled or selective
Route is advertised when virtual-address is available.
disabled
Route is not advertised.
always
Route is advertised regardless of the availability status.
any Route is advertised when any of the contributing virtual
server is available.
all Route is advertised when all of the contributing virtual
Because the previous commands are also base configuration you should save the configuration on both devices.
Now you can begin to configure the routing protocol in ZebOS. To reach the ZebOS CLI, from the BIG-IP BASH shell.
[root@W_B_BIGIP-13:Active:In Sync] config # imish
[root@W_B_BIGIP-13:Active:In Sync] config # enable
W_B_BIGIP-13.local[0]#show ip route
Codes: K - kernel, C - connected, S - static, R - RIP, B - BGP
        O - OSPF, IA - OSPF inter area
        N1 - OSPF NSSA external type 1, N2 - OSPF NSSA external type 2
        E1 - OSPF external type 1, E2 - OSPF external type 2
        i - IS-IS, L1 - IS-IS level-1, L2 - IS-IS level-2, ia - IS-IS inter area
        * - candidate default
C       10.1.10.0/24 is directly connected, external
C       10.1.20.0/24 is directly connected, internal
K       10.3.99.0/24 [0/0] via 10.1.20.254, internal
K       10.99.99.100/32 [0/0] is directly connected, tmm
C       127.0.0.1/32 is directly connected, lo
C       127.1.1.254/32 is directly connected, tmm
C       192.168.255.0/24 is directly connected, ha
Gateway of last resort is not set
[root@W_A_BIGIP-13:Active:In Sync] config # imish
[root@W_A_BIGIP-13:Active:In Sync] config # enable
W_A_BIGIP-13.local[0]>sh ip route
Note
The two kernel routes designated with a 'K'. These are routes provided to ZebOS from tmm. The first route you may recall is 10.3.99.0/24. This is the static route you configured via tmsh. The second route, 10.99.99.100/32 is the virtual server.
Note
Why does the kernel route for 10.99.99.0/32 only show up in one of the devices?
Force a failover event to occur on the 'Active' device and validate.
W_B_BIGIP-13.local[0]#quit
tmsh run sys failover standby
Note
This needs to be run from whichever device in your HA Pair is currently active. Once you 'quit' imish, it can be determined from the bash shell prompt.
[root@W_A_BIGIP-13:Active:In Sync] [root@W_B_BIGIP-13:Active:In Sync]
W_B_BIGIP-13.local[0]#sh ip route
W_A_BIGIP-13.local[0]#show ip route
Configure the iBGP session with the West CPE devices W_CPE_A_CSR1k and W_CPE_A_CSR1k. The CPE configuration is already done for you so you only need to configure the two BIG-IP devices.
W_A_BIGIP-13.local[0]>enable
W_A_BIGIP-13.local[0]#config t
W_A_BIGIP-13.local[0](config)#router bgp 65101
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.3 remote-as 65101
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.3 description W_CPE_A
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.4 remote-as 65101
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.4 description W_CPE_B
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.6 remote-as 65101
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.6 description W_B_BIGIP-13
W_A_BIGIP-13.local[0](config-router)# redistribute kernel
W_A_BIGIP-13.local[0](config)#end
W_A_BIGIP-13.local[0]#wr
Building configuration...
[OK]
W_B_BIGIP-13.local[0]>enable
W_B_BIGIP-13.local[0]#config t
W_B_BIGIP-13.local[0](config)#router bgp 65101
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.3 remote-as 65101
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.3 description W_CPE_A
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.4 remote-as 65101
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.4 description W_CPE_B
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.5 remote-as 65101
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.5 description W_A_BIGIP-13
W_B_BIGIP-13.local[0](config-router)#redistribute kernel
W_B_BIGIP-13.local[0](config-router)#end
W_B_BIGIP-13.local[0]#wr
[OK]
Note
BGP has not come up between the BIG-IP's. Why is that?
W_A_BIGIP-13.local[0]#sh ip bgp summary
BGP router identifier 192.168.255.10, local AS number 65101
BGP table version is 3
4 BGP AS-PATH entries
0 BGP community entries
Neighbor        V    AS MsgRcvd MsgSent   TblVer  InQ OutQ Up/Down  State/PfxRcd
10.1.10.3       4 65101      41      32        3    0    0 00:00:26        6
10.1.10.4       4 65101      40      30        3    0    0 00:00:26        6
10.1.10.6       4 65101       7       7        0    0    0 00:01:04 Active
Configure port lockdown on BIG-IP's to allow BGP via external interface on both BIG-IP:
tmsh list net self external allow-service
    net self external {
        allow-service none
tmsh modify net self external allow-service add { tcp:179 }
    net self external {
        allow-service {
            tcp:bgp
Validate BGP is now established between both BIGIP's
W_B_BIGIP-13.local[0]#sh ip bgp summary
BGP router identifier 192.168.255.11, local AS number 65101
BGP table version is 5
10.1.10.3       4 65101      32      23        5    0    0 00:03:16        6
10.1.10.4       4 65101      32      23        5    0    0 00:03:16        6
10.1.10.5       4 65101      12      11        5    0    0 00:00:07        2
Total number of neighbors 3
Note
iBGP requires that you configure a full mesh. But in this simplified scenario you do not need to configure a full mesh for iBGP because there are only four routers and you've got the BIG-IP HA Cluster and your outbound gateway. Your topology may vary and you may want to configure a full mesh if there are other devices. Additionally in a larger topology you may want to configure eBGP between the CPE and the BIG-IP clusters. This is explored in more depth when you configure the East data center.
Note
The redistribute kernel command is the secret sauce that allows tmm routes from the BIG-IP to be advertised to BGP peers.
Validate that the website is accessible from the jumphost
root@jumphost:~# curl 10.99.99.100
<html><body><h1>It works!</h1>
<p>This is the default web page for this server.</p>
<p>The web server software is running but no content has been added, yet.</p>
</body></html>
Validate your configuration on both of the CPE routers
You can telnet to either of the CPE devices
csr1000v-W_CPE_A#sh ip route
Codes: L - local, C - connected, S - static, R - RIP, M - mobile, B - BGP
        D - EIGRP, EX - EIGRP external, O - OSPF, IA - OSPF inter area
        i - IS-IS, su - IS-IS summary, L1 - IS-IS level-1, L2 - IS-IS level-2
        ia - IS-IS inter area, * - candidate default, U - per-user static route
        o - ODR, P - periodic downloaded static route, H - NHRP, l - LISP
        a - application route
        + - replicated route, % - next hop override, p - overrides from PfR
        1.0.0.0/32 is subnetted, 2 subnets
C        1.1.1.1 is directly connected, Loopback100
O        1.1.1.2 [110/2] via 10.1.10.4, 02:49:46, GigabitEthernet4
        3.0.0.0/32 is subnetted, 1 subnets
B        3.3.3.3 [20/0] via 172.16.1.3, 00:05:44
        10.0.0.0/8 is variably subnetted, 5 subnets, 2 masks
C        10.1.10.0/24 is directly connected, GigabitEthernet4
L        10.1.10.3/32 is directly connected, GigabitEthernet4
B        10.99.99.100/32 [200/0] via 10.1.10.5, 00:00:07
        172.16.0.0/16 is variably subnetted, 6 subnets, 2 masks
C        172.16.1.0/24 is directly connected, GigabitEthernet2
L        172.16.1.4/32 is directly connected, GigabitEthernet2
B        172.16.2.0/24 [20/0] via 172.16.1.3, 00:35:33
C        172.16.3.0/24 is directly connected, GigabitEthernet3
L        172.16.3.4/32 is directly connected, GigabitEthernet3
B        172.16.6.0/24 [20/0] via 172.16.1.3, 00:49:06
Note
The BGP route should be pointing to the 'Active' device in the HA cluster.
Initiate a failover event to determine how the route update happens.
From whichever BIG-IP device is active:
O        1.1.1.2 [110/2] via 10.1.10.4, 02:51:26, GigabitEthernet4
B        3.3.3.3 [20/0] via 172.16.1.3, 00:07:24
B        10.99.99.100/32 [200/0] via 10.1.10.6, 00:00:02
B        172.16.2.0/24 [20/0] via 172.16.1.3, 00:37:13
B        172.16.6.0/24 [20/0] via 172.16.1.3, 00:50:46
Note
If you were watching the update time you'll notice it takes a bit for the next-hop address to change. This can be modified with timers, or you can use a floating self-ip between an HA pair of BIG-IP's to minimize the update time because the Next-hop entry for the floating address never needs to be updated.
</body></html>
Next we will configure a floating self-ip address to minimize the need for the next-hop to change. On one of the West Data Center BIG-IP devices. Combined with mac-masquerading and connection mirroring this is the least disruptive failover configuration.
tmsh create net self float-bgp address 10.1.10.7/24 vlan external traffic-group traffic-group-1
You can either wait until the route update occurs or you can reset the BGP neighbors with the clear ip bgp * command
W_B_BIGIP-13.local[0]#clear ip bgp *
O        1.1.1.2 [110/2] via 10.1.10.4, 00:31:23, GigabitEthernet4
        2.0.0.0/32 is subnetted, 1 subnets
B        2.2.2.2 [20/0] via 172.16.1.3, 00:30:43
        10.0.0.0/8 is variably subnetted, 3 subnets, 2 masks
B        10.99.99.100/32 [200/0] via 10.1.10.7, 00:03:06
B        172.16.2.0/24 [20/0] via 172.16.1.3, 00:30:44
B        172.16.6.0/24 [20/0] via 172.16.1.3, 00:30:44
On the CPE devices look at the result of the show ip bgp command
csr1000v-W_CPE_A#sh ip bgp
BGP table version is 10, local router ID is 1.1.1.1
Status codes: s suppressed, d damped, h history, * valid, > best, i - internal,
                r RIB-failure, S Stale, m multipath, b backup-path, f RT-Filter,
                x best-external, a additional-path, c RIB-compressed,
                t secondary path,
Origin codes: i - IGP, e - EGP, ? - incomplete
RPKI validation codes: V valid, I invalid, N Not found
        Network          Next Hop            Metric LocPrf Weight Path
    *>   1.1.1.1/32       0.0.0.0                  0         32768 i
    r>i  1.1.1.2/32       1.1.1.2                  0    100      0 i
    * i  2.2.2.2/32       172.16.2.3               0    100      0 65001 65002 65201 i
    *>                    172.16.1.3                             0 65001 65002 65201 i
    * i  10.3.99.0/24     10.1.20.254                   100      0 ?
    *>i  10.99.99.100/32  10.1.10.7                     100      0 ?
    r i  172.16.1.0/24    172.16.2.3               0    100      0 65001 ?
    r>                    172.16.1.3               0             0 65001 ?
    * i  172.16.2.0/24    172.16.2.3               0    100      0 65001 ?
    *>                    172.16.1.3               0             0 65001 ?
    * i  172.16.6.0/24    172.16.2.3               0    100      0 65001 65002 ?
    *>                    172.16.1.3                             0 65001 65002 ?
csr1000v-W_CPE_A#
Note
Compare the show ip route output in the previous step to the show ip bgp output. What looks out of place here? Why is it there? Why does it not show up in the routing table?
Create an aggregate route since many service providers will not accept anything less than a /24
On both of the West BIG-IPs configure ZebOS to only advertise an aggregate route for the virtual server network and filter out the core network advertisement.
W_A_BIGIP-13.local[0](config)#ip prefix-list PFX_ALLOW_VIPS seq 5 permit 10.99.99.0/24
W_A_BIGIP-13.local[0](config)#route-map RESTRICT_ADVERTISE permit 10
W_A_BIGIP-13.local[0](config-route-map)# match ip address prefix-list PFX_ALLOW_VIPS
W_A_BIGIP-13.local[0](config-router)# aggregate-address 10.99.99.0/24
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.3 route-map RESTRICT_ADVERTISE out
W_A_BIGIP-13.local[0](config-router)# neighbor 10.1.10.4 route-map RESTRICT_ADVERTISE out
W_A_BIGIP-13.local[0](config-router)#end
[OK]
W_B_BIGIP-13.local[0]# config t
W_B_BIGIP-13.local[0](config)#ip prefix-list PFX_ALLOW_VIPS seq 5 permit 10.99.99.0/24
W_B_BIGIP-13.local[0](config)#route-map RESTRICT_ADVERTISE permit 10
W_B_BIGIP-13.local[0](config-route-map)# match ip address prefix-list PFX_ALLOW_VIPS
W_B_BIGIP-13.local[0](config-router)# aggregate-address 10.99.99.0/24
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.3 route-map RESTRICT_ADVERTISE out
W_B_BIGIP-13.local[0](config-router)# neighbor 10.1.10.4 route-map RESTRICT_ADVERTISE out
[OK]
Validate on either of the CPE routers. You can either wait until the route update occurs or you can reset the BGP neighbors with the clear ip bgp * command
Clear ip bgp * on the active BIG-IP such that /32 is no longer advertised.
O        1.1.1.2 [110/2] via 10.1.10.4, 03:04:37, GigabitEthernet4
B        2.2.2.2 [20/0] via 172.16.1.3, 00:06:50
B        10.99.99.0/24 [200/0] via 10.1.10.7, 00:06:50
B        172.16.2.0/24 [20/0] via 172.16.1.3, 00:06:50
B        172.16.6.0/24 [20/0] via 172.16.1.3, 00:06:50
Validate that the website is accessible from the jumphost.
</body></html>
Add another virtual server and test the behavior of failover of the aggregate route.
Add another virtual server within the VIP subnet.
tmsh create ltm pool pool2 members add { 10.3.99.200:8081 } monitor tcp_half_open
tmsh create ltm virtual vip2 destination 10.99.99.101:80 source-address-translation { type automap } pool pool2 profiles add { tcp http }
root@jumphost:~# curl 10.99.99.101
</body></html>
Disable the first pool you created.
tmsh modify ltm pool pool1 members modify { 10.3.99.200:http { state user-down } }
tmsh show ltm virtual vip1
Status
        State            : enabled
        CMP              : enabled
        CMP Mode         : all-cpus
Validate that the website is still accessible from the jumphost
curl: (7) Failed to connect to 10.99.99.101 port 80: No route to host
Now look at the routing table on the CPE virtual server.
O        1.1.1.2 [110/2] via 10.1.10.4, 00:57:32, GigabitEthernet4
B        2.2.2.2 [20/0] via 172.16.1.3, 00:15:52
        10.0.0.0/8 is variably subnetted, 2 subnets, 2 masks
B        172.16.2.0/24 [20/0] via 172.16.1.3, 00:56:56
B        172.16.6.0/24 [20/0] via 172.16.1.3, 00:56:56
On the active BIG-IP look at the routing table.
B       1.1.1.1/32 [200/0] via 10.1.10.3, external, 00:57:35
B       1.1.1.2/32 [200/0] via 10.1.10.4, external, 00:57:35
Note
There are no kernel routes from tmm. e.g. 10.99.99.0/24, 10.99.99.100, or 10.99.99.101.
Why?
Note
You need to make sure either all virtual-addresses have advertisement-enabled or a healthy majority of them enabled or the aggregate route will be withdrawn. BGP by default needs to have a route from another routing protocol available in order to advertise a route to a BGP neighbor. In this case because only one of the virtual-addresses has it enabled and it goes down, all other addresses within the /24 are considered unreachable and so the route is withdrawn.
Re-enable the pool and then review the BIG-IP and CPE route tables.
tmsh modify ltm pool pool1 members modify { 10.3.99.200:http { state user-up } }
B       1.1.1.1/32 [200/0] via 10.1.10.3, external, 00:58:09
B       1.1.1.2/32 [200/0] via 10.1.10.4, external, 00:58:09
B       10.99.99.0/24 [200/0] is a summary, Null, 00:00:04
O        1.1.1.2 [110/2] via 10.1.10.4, 01:10:54, GigabitEthernet4
B        2.2.2.2 [20/0] via 172.16.1.3, 00:29:14
B        10.99.99.0/24 [200/0] via 10.1.10.7, 00:09:42
B        172.16.2.0/24 [20/0] via 172.16.1.3, 01:10:18
B        172.16.6.0/24 [20/0] via 172.16.1.3, 01:10:18
Validate that the websites are accessible from the jumphost
</body></html>
</body></html>
Modify the virtual-address for the second virtual server to allow route-advertisement and repeat disabling.
tmsh modify ltm virtual-address 10.99.99.101 route-advertisement selective
O        1.1.1.2 [110/2] via 10.1.10.4, 01:21:27, GigabitEthernet4
B        2.2.2.2 [20/0] via 172.16.1.3, 00:39:47
B        10.99.99.0/24 [200/0] via 10.1.10.7, 00:20:15
B        172.16.2.0/24 [20/0] via 172.16.1.3, 01:20:51
B        172.16.6.0/24 [20/0] via 172.16.1.3, 01:20:51
The route now remained when one of the virtual servers went down.
Validate that .101 website remained up while the .100 is not.
curl: (56) Recv failure: Connection reset by peer
</body></html>
You can re-enable the .100 website before moving on to Module 2.
</body></html>
</body></html>
Sample configuration
Sample complete configuration from one BIG-IP:
        W_B_BIGIP-13.local[0]#sh run
        no service password-encryption
        router bgp 65101
            redistribute kernel
        line con 0
            login
        line vty 0 39
            login
        end
Note
This completes Lab 1