F5 Application Delivery Controller Solutions > Resilient Data Center Architectures with F5 BIG-IP > Module 1 – Resilient Data Center Architectures Source | Edit on
Lab 2: East Data Center Configuration¶
In this lab you will be configuring two BIG-IP standalone devices and setting it up to advertise available virtual servers through the BGP protocol.
Configure the BIG-IP East Data Center¶
From the jumphost ssh to the E_A_BIGIP-13
From the jumphost ssh to the E_B_BIGIP-13
Save the configuration on both devices
Configure the eBGP session between E_A_BIGIP-13 and the East Core via csr1000v-CORE.¶
Note
The CORE Router configuration is already done for you so you only need to configure the two EAST BIG-IP devices.
E_A_BIGIP-13: On E_A_BIGIP configure the following to enable BGP for route-domain 0.
E_A_BIGIP-13: Bring up BGP with the East Core and configure the keepalive interval to 3 seconds and hold time to 9 seconds via neighbor statement instead of using the default values of 30 seconds for keepalive and 180 seconds for hold time:
[root@E_A_BIGIP-13:Active:In Sync] config # imish -r 0
E_A_BIGIP-13.local[0]>enable
E_A_BIGIP-13.local[0]#config t
E_A_BIGIP-13.local[0](config)#router bgp 65202
E_A_BIGIP-13.local[0](config-router)# neighbor 10.2.40.4 remote-as 65205
E_A_BIGIP-13.local[0](config-router)# neighbor 10.2.40.4 description E_CORE
E_A_BIGIP-13.local[0](config-router)# neighbor 10.2.40.4 timers 3 9
E_A_BIGIP-13.local[0](config-router)# end
E_A_BIGIP-13.local[0]#write mem
E_A_BIGIP-13: Verify eBGP adjacencies are up between E_A_BIGIP-13 and the East Core router - csr1000v-CORE.
E_A_BIGIP-13: Verify route for the webservice via 10.3.99.0/24 is installed in routing table after eBGP is established between E_A_BIGIP-13 and the East Core router - csr1000v-CORE.
Configure the eBGP session between E_B_BIGIP-13 and the East Core via csr1000v-CORE.¶
Note
E_B_BIGIP-13: On E_B_BIGIP configure the following to enable BGP for route-domain 0.
E_B_BIGIP-13: Bring up BGP with the East Core and configure the keepalive interval to 3 seconds and hold time to 9 seconds via neighbor statement instead of using the default values of 30 seconds for keepalive and 180 seconds for hold time:
[root@E_B_BIGIP-13:Active:In Sync] config # imish -r 0
E_B_BIGIP-13.local[0]>enable
E_B_BIGIP-13.local[0]#config t
E_B_BIGIP-13.local[0](config)#router bgp 65203
E_B_BIGIP-13.local[0](config-router)# neighbor 10.2.50.4 remote-as 65205
E_B_BIGIP-13.local[0](config-router)# neighbor 10.2.50.4 description E_CORE
E_B_BIGIP-13.local[0](config-router)# neighbor 10.2.50.4 timers 3 9
E_B_BIGIP-13: Verify eBGP adjacencies are up between E_B_BIGIP-13 and the East Core router - csr1000v-CORE.
E_B_BIGIP-13.local[0]#sh ip bgp sum
BGP router identifier 10.2.50.3, local AS number 65203
BGP table version is 2
1 BGP AS-PATH entries
0 BGP community entries
Neighbor V AS MsgRcvd MsgSent TblVer InQ OutQ Up/Down State/PfxRcd
10.2.50.4 4 65205 4 2 1 0 0 00:00:16 2
Total number of neighbors 1
E_B_BIGIP-13: Verify route for the webservice via 10.3.99.0/24 is installed in routing table after eBGP is established between E_B_BIGIP-13 and the East Core router - csr1000v-CORE.
Validate Webserver Connectivity via Core Network:¶
Verify that you can reach the webserver on the core network with icmp ping and curl from both BIG-IPs.
E_A_BIGIP-13: Ping the webserver @ 10.3.99.200 via the core network from E_A_BIGIP-13. Note the ping may not work immediately and could take a few seconds. Also Note the escape sequence for icmp ping on the BIGIP is “CTRL + C”
[root@E_A_BIGIP-13:Active:Standalone] config # ping 10.3.99.200
PING 10.3.99.200 (10.3.99.200) 56(84) bytes of data.
64 bytes from 10.3.99.200: icmp_seq=1 ttl=63 time=8.51 ms
64 bytes from 10.3.99.200: icmp_seq=2 ttl=63 time=8.12 ms
^C
--- 10.3.99.200 ping statistics ---
2 packets transmitted, 2 received, 0% packet loss, time 1823ms
rtt min/avg/max/mdev = 8.121/8.318/8.516/0.217 ms
E_A_BIGIP-13: Curl the webserver @ 10.3.99.200 via the core network from E_A_BIGIP-13.
E_B_BIGIP-13: Ping the webserver @ 10.3.99.200 via the core network from E_B_BIGIP-13. Note the ping may not work immediately and could take a few seconds. Also Note the escape sequence for icmp ping on the BIGIP is “CTRL + C”
[root@E_B_BIGIP-13:Active:Standalone] config # ping 10.3.99.200
64 bytes from 10.3.99.200: icmp_seq=1 ttl=63 time=6.06 ms
64 bytes from 10.3.99.200: icmp_seq=2 ttl=63 time=9.31 ms
^C
2 packets transmitted, 2 received, 0% packet loss, time 1726ms
rtt min/avg/max/mdev = 6.068/7.692/9.317/1.626 ms
E_B_BIGIP-13: Curl the webserver @ 10.3.99.200 via the core network from E_B_BIGIP-13.
Create an application configuration for a virtual server and a pool member on E_A_BIGIP-13:¶
E_A_BIGIP-13: Create the following virtual server and pool member on E_A_BIGIP-13:
E_A_BIGIP-13: Your virtual server should now show available on E_A_BIGIP-13:
[root@E_A_BIGIP-13:Active:Standalone] config # tmsh show ltm virtual
Ltm::Virtual Server: vip1
Status
Availability : available
State : enabled
Reason : The virtual server is available
CMP : enabled
CMP Mode : all-cpus
Destination : 10.99.99.102:80
Configure the route advertisement on the E_A_BIGIP-13:¶
E_A_BIGIP-13: Configure the eBGP session on E_A_BIGIP to East CPE_A. The CPE configuration is already done for you so you only need to configure the BIGIP side of session.
E_A_BIGIP-13.local[0](config-router)# neighbor 10.2.20.4 remote-as 65201
E_A_BIGIP-13.local[0](config-router)# neighbor 10.2.20.4 description E_CPE_A
E_A_BIGIP-13.local[0](config-router)# neighbor 10.2.20.4 timers 3 9
E_A_BIGIP-13: Verify eBGP adjacencies are up between E_A_BIGIP_13 and the East CPE_A.
E_A_BIGIP-13.local[0]#sh ip bgp sum
BGP router identifier 10.2.40.3, local AS number 65202
BGP table version is 3
5 BGP AS-PATH entries
10.2.20.4 4 65201 27 21 3 0 0 00:00:53 8
10.2.40.4 4 65205 157 141 3 0 0 01:07:25 2
E_A_BIGIP-13: On E_A_BIGIP configure the following network statement for 10.99.99.0/24 such that prefix is originated locally:
[root@E_A_BIGIP-13:Active:Standalone] config # imish -r 0
E_A_BIGIP-13.local[0]#conf t
Enter configuration commands, one per line. End with CNTL/Z.
E_A_BIGIP-13.local[0](config-router)#network 10.99.99.0/24
E_A_BIGIP-13.local[0](config-router)#end
E_A_BIGIP-13: On E_A_BIGIP verify 10.99.99.0/24 is being locally originated which can be seen with “Local”:
E_A_BIGIP-13: On E_A_BIGIP verify 10.99.99.0/24 is being advertised outbound to East CPE device via E_CPE_A_CSR1k:
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is learning the 10.99.99.0/24 inbound from E_A_BIGIP:
Note
You can telnet to the CPE devices using the BGP neighbor IP address from Zebos using root/default for user/pass:
Example telnet from E_A_BIGIP-13 to East CPE Device @ 10.2.20.4:
E_CPE_A_CSR1k: Continued...Verify that E_CPE_A_CSR1k is learning the 10.99.99.0/24 inbound from E_A_BIGIP:
csr1000v-E_CPE_A>show ip bgp vpnv4 vrf internet neighbors 10.2.20.3 routes
BGP table version is 26, local router ID is 2.2.2.2
Status codes: s suppressed, d damped, h history, * valid, > best, i - internal,
r RIB-failure, S Stale, m multipath, b backup-path, f RT-Filter,
x best-external, a additional-path, c RIB-compressed,
t secondary path,
Origin codes: i - IGP, e - EGP, ? - incomplete
RPKI validation codes: V valid, I invalid, N Not found
Network Next Hop Metric LocPrf Weight Path
Route Distinguisher: 65201:1000 (default for vrf internet)
*> 3.3.3.3/32 10.2.20.3 4294967295 0 65202 65205 i
*> 10.99.99.0/24 10.2.20.3 4294967295 0 65202 i
Total number of prefixes 2
csr1000v-E_CPE_A>
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is installing 10.99.99.0/24 from E_A_BIGIP:
csr1000v-E_CPE_A>show ip route vrf internet
Routing Table: internet
Codes: L - local, C - connected, S - static, R - RIP, M - mobile, B - BGP
D - EIGRP, EX - EIGRP external, O - OSPF, IA - OSPF inter area
N1 - OSPF NSSA external type 1, N2 - OSPF NSSA external type 2
E1 - OSPF external type 1, E2 - OSPF external type 2
i - IS-IS, su - IS-IS summary, L1 - IS-IS level-1, L2 - IS-IS level-2
ia - IS-IS inter area, * - candidate default, U - per-user static route
o - ODR, P - periodic downloaded static route, H - NHRP, l - LISP
a - application route
+ - replicated route, % - next hop override, p - overrides from PfR
Gateway of last resort is not set
1.0.0.0/32 is subnetted, 2 subnets
B 1.1.1.1 [20/4294967294] via 172.16.6.3, 22:12:30
B 1.1.1.2 [20/4294967294] via 172.16.6.3, 22:12:32
3.0.0.0/32 is subnetted, 1 subnets
B 3.3.3.3 [20/4294967294] via 10.2.20.3, 01:27:19
10.0.0.0/8 is variably subnetted, 5 subnets, 2 masks
C 10.2.20.0/24 is directly connected, GigabitEthernet2
L 10.2.20.4/32 is directly connected, GigabitEthernet2
C 10.2.30.0/24 is directly connected, GigabitEthernet3
L 10.2.30.4/32 is directly connected, GigabitEthernet3
B 10.99.99.0/24 [20/4294967294] via 10.2.20.3, 01:22:58
99.0.0.0/24 is subnetted, 1 subnets
B 99.99.99.0 [20/4294967294] via 172.16.6.3, 22:13:59
172.16.0.0/16 is variably subnetted, 5 subnets, 2 masks
B 172.16.1.0/24 [20/4294967294] via 172.16.6.3, 22:12:40
B 172.16.2.0/24 [20/4294967294] via 172.16.6.3, 22:12:40
C 172.16.6.0/24 is directly connected, GigabitEthernet5
L 172.16.6.4/32 is directly connected, GigabitEthernet5
B 172.16.99.0/24 [20/0] via 172.16.6.3, 22:13:59
csr1000v-E_CPE_A>
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is installing specific 10.99.99.0/24 from E_A_BIGIP using specific ip route command:
csr1000v-E_CPE_A#sh ip route vrf internet 10.99.99.0 255.255.255.0
Routing entry for 10.99.99.0/24
Known via "bgp 65201", distance 20, metric 4294967294
Tag 65202, type external
Last update from 10.2.20.3 00:00:02 ago
Routing Descriptor Blocks:
* 10.2.20.3, from 10.2.20.3, 00:00:02 ago
Route metric is 4294967294, traffic share count is 1
AS Hops 1
Route tag 65202
MPLS label: none
csr1000v-SP_C: Verify that csr1000v-SP_C is installing 10.99.99.0/24 via East DC because Origin attribute is IGP versus incomplete via for West DC:
You can telnet to csr1000v-SP_C from the jumpbox @ 192.168.1.15 with root/default user/pass:
csr1000v-SP_C: Verify that csr1000v-SP_C is installing 10.99.99.0/24 in BGP table via East DC. Note the Best path is via AS 65002 988.
csr1000v-SP_C>sh ip bgp 10.99.99.0/24
BGP routing table entry for 10.99.99.0/24, version 16
Paths: (2 available, best #1, table default)
Advertised to update-groups:
1
Refresh Epoch 1
65002 988
172.16.99.4 from 172.16.99.4 (172.1.1.2)
Origin IGP, localpref 100, valid, external, best
rx pathid: 0, tx pathid: 0x0
Refresh Epoch 1
65001 65101, (aggregated by 65101 192.168.255.10)
172.16.99.3 from 172.16.99.3 (172.1.1.1)
Origin incomplete, localpref 100, valid, external, atomic-aggregate
Note
The BGP peering between E_CPE_A and SP_B leverages AS 988 as seen below. The following command replaces the local private AS Path with 988 for prefixes originated from East DC to the SP Cloud.
csr1000v-SP_C: Verify that csr1000v-SP_C is installing 10.99.99.0/24 in the ip routing table:
csr1000v-SP_C>sh ip route 10.99.99.0 255.255.255.0
Known via "bgp 65003", distance 20, metric 0
Tag 65002, type external
Last update from 172.16.99.4 00:18:45 ago
* 172.16.99.4, from 172.16.99.4, 00:18:45 ago
Route metric is 0, traffic share count is 1
AS Hops 2
Route tag 65002
MPLS label: none
Note
From the jump host you can now try to reach the website via E_A_BIGIP and validate the path is installed via EAST DC.
Either open a web browser and browse to http://10.99.99.102 or from the jumpbox CLI, type:
curl http://10.99.99.102
Jumpbox: Curl from the jumphost to the virtual server.
Jumpbox: Traceroute from the jumphost to the virtual server to verify the path it is taking.
root@jumphost:~# traceroute 10.99.99.102
traceroute to 10.99.99.102 (10.99.99.102), 30 hops max, 60 byte packets
1 192.168.1.15 (192.168.1.15) 7.202 ms 8.251 ms 8.049 ms
2 172.16.99.4 (172.16.99.4) 22.485 ms 23.834 ms 36.059 ms
3 172.16.6.4 (172.16.6.4) 40.575 ms 40.425 ms 62.741 ms
4 10.99.99.102 (10.99.99.102) 64.284 ms 64.026 ms 91.206 ms
root@jumphost:~#
E_CPE_A_CSR1k: You can also validate from the CPE with telnet to 10.99.99.102 on port 80. Note that you can clear the telnet session by executing “clear line vty 0” on the console of the CPE:
csr1000v-SP_C: You can also validate via traceroute to 10.99.99.102 on SP_C:
csr1000v-SP_C>traceroute 10.99.99.102
Type escape sequence to abort.
Tracing the route to 10.99.99.102
VRF info: (vrf in name/id, vrf out name/id)
1 172.16.99.4 [AS 65001] 7 msec 5 msec 9 msec
2 172.16.6.4 [AS 65002] 10 msec 10 msec 14 msec
3 10.99.99.102 [AS 988] 13 msec 13 msec 15 msec
csr1000v-SP_C>
Note
Now lets move on and configure BGP on E_B_BIGIP.....
Create an application configuration for a virtual server and a pool member on E_B_BIGIP-13:¶
E_B_BIGIP-13: Create the following virtual server and pool member on E_B_BIGIP-13:
E_B_BIGIP-13: Your virtual server should now show available on E_B_BIGIP-13:
[root@E_B_BIGIP-13:Active:Standalone] config # tmsh show ltm virtual
Status
State : enabled
CMP : enabled
CMP Mode : all-cpus
Configure the route advertisement on the E_B_BIGIP-13:¶
E_B_BIGIP-13: Configure the eBGP session on E_B_BIGIP-13 to East CPE_A. The CPE configuration is already done for you so you only need to configure the BIG-IP side of session.
E_B_BIGIP-13.local[0](config-router)# neighbor 10.2.30.4 remote-as 65201
E_B_BIGIP-13.local[0](config-router)# neighbor 10.2.30.4 description E_CPE_A
E_B_BIGIP-13.local[0](config-router)# neighbor 10.2.30.4 timers 3 9
E_B_BIGIP-13: Verify eBGP adjacencies are up between E_B_BIGIP-13 and the East CPE router - E_CPE_A_CSR1k.
BGP table version is 6
12 BGP AS-PATH entries
10.2.30.4 4 65201 17 14 5 0 0 00:00:18 9
10.2.50.4 4 65205 385 350 6 0 0 02:52:20 10
Total number of neighbors 2
E_B_BIGIP-13: On E_B_BIGIP configure the following network statement for 10.99.99.0/24 such that prefix is originated locally:
[root@E_B_BIGIP-13:Active:Standalone] config # imish -r 0
E_B_BIGIP-13.local[0]#conf t
E_B_BIGIP-13.local[0](config-router)#network 10.99.99.0/24
E_B_BIGIP-13.local[0](config-router)#end
E_B_BIGIP-13.local[0]#wr
Building configuration...
[OK]
E_B_BIGIP-13: On E_B_BIGIP verify 10.99.99.0/24 is being locally originated which can be seen with “Local”:
E_B_BIGIP-13.local[0]#sh ip bgp 10.99.99.0/24 | b Local
...skipping
Local
0.0.0.0 from 0.0.0.0 (10.2.50.3)
Origin IGP, localpref 100, weight 32768, valid, sourced, local, best
Last update: Mon Jul 16 19:29:34 2018
65201 65202
10.2.30.4 from 10.2.30.4 (2.2.2.2)
Origin IGP metric 0, localpref 100, valid, external
Last update: Mon Jul 16 19:02:03 2018
65205 65202
10.2.50.4 from 10.2.50.4 (3.3.3.3)
E_B_BIGIP-13: On E_B_BIGIP verify 10.99.99.0/24 is being advertised outbound to East CPE device via E_CPE_A_CSR1k:
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is learning the 10.99.99.0/24 inbound from E_B_BIGIP:
Note: You can telnet to the CPE devices using the BGP neighbor IP address from Zebos using root/default for user/pass:
Example telnet from E_B_BIGIP-13 to East CPE Device @ 10.2.30.4:
E_CPE_A_CSR1k: Continued...Verify that E_CPE_A_CSR1k is learning the 10.99.99.0/24 inbound from E_B_BIGIP:
csr1000v-E_CPE_A>show ip bgp vpnv4 vrf internet neighbors 10.2.30.3 routes
BGP table version is 28, local router ID is 2.2.2.2
t secondary path,
*m 3.3.3.3/32 10.2.30.3 4294967295 0 65203 65205 i
*m 10.99.99.0/24 10.2.30.3 4294967295 0 65203 i
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is installing 10.99.99.0/24 from E_B_BIGIP using ip route command. Notice the next hop of E_A_BIGIP @ 10.2.20.3 & E_B_BIGIP @ 10.2.30.3:
csr1000v-E_CPE_A>sh ip route vrf internet
B 1.1.1.1 [20/4294967294] via 172.16.6.3, 23:39:09
B 1.1.1.2 [20/4294967294] via 172.16.6.3, 23:39:11
B 3.3.3.3 [20/4294967294] via 10.2.30.3, 00:37:06
[20/4294967294] via 10.2.20.3, 00:37:06
B 10.99.99.0/24 [20/4294967294] via 10.2.30.3, 00:34:33
[20/4294967294] via 10.2.20.3, 00:34:33
B 99.99.99.0 [20/4294967294] via 172.16.6.3, 23:40:38
B 172.16.1.0/24 [20/4294967294] via 172.16.6.3, 23:39:19
B 172.16.2.0/24 [20/4294967294] via 172.16.6.3, 23:39:19
B 172.16.99.0/24 [20/0] via 172.16.6.3, 23:40:38
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is now installing specific 10.99.99.0/24 from E_B_BIGIP using specific ip route command. Notice the next hop of E_A_BIGIP @ 10.2.20.3 & E_B_BIGIP @ 10.2.30.3:
csr1000v-E_CPE_A>sh ip route vrf internet 10.99.99.0 255.255.255.0
Last update from 10.2.20.3 00:39:40 ago
* 10.2.30.3, from 10.2.30.3, 00:39:40 ago
AS Hops 1
Route tag 65202
MPLS label: none
10.2.20.3, from 10.2.20.3, 00:39:40 ago
AS Hops 1
Route tag 65202
MPLS label: none
csr1000v-E_CPE_A>
Note
Congratulations! You now have eBGP Multipath Loadsharing working within the East DC! As seen above, this will trigger ECMP for 10.99.99.0/24 on E_CPE_A_CSR1k towards E_A_BIGIP and E_B_BIGIP. Note that normally the weight, local preference, AS path length, origin, med, etc. would need to be the same for the parallel routes to be installed in the routing table.
It is worth noting that this behavior various from version to version of IOS. In this lab, we are using IOS-XE Version 16.3.6. With this version, the entire AS path needs to be the same for multipath condition to be met.
How did we work around this? The following hidden command is used on the CPE to ignore the different AS Path and install the route as multipath if all other conditions are met:
csr1000v-SP_C: Verify that nothing changed on csr1000v-SP_C and it is still installing 10.99.99.0/24 via East DC because Origin attribute is IGP versus incomplete for West DC:
csr1000v-SP_C: Verify that csr1000v-SP_C is installing 10.99.99.0/24 in BGP table via East DC. Recall the Best path leveraging EAST DC is via AS 65002 988.
1
Refresh Epoch 1
65002 988
Refresh Epoch 1
AS Hops 2
Route tag 65002
MPLS label: none
Note
As seen above, all traffic from the Jumpbox via SP_C destined to 10.99.99.0/24 is currently via the East DC. This is because EAST DC wins the tiebreaker as the Origin attribute is IGP versus incomplete for West DC
At this moment, you can only curl to 10.99.99.102 VIP in the EAST DC via the jumpbox.
Place E_A_BIGIP into maintenance mode within the East DC by using BGP AS Path Prepending:¶
E_A_BIGIP-13: Create AS-Path-Prepend-OUT route-map on E_A_BIGIP for 10.99.99.0/24 to insert 1 AS Path prepend into the prefix:
E_A_BIGIP-13.local[0](config)#ip prefix-list as-path-prepend-prefix seq 10 permit 10.99.99.0/24
E_A_BIGIP-13.local[0](config)#route-map AS-Path-Prepend-OUT permit 100
E_A_BIGIP-13.local[0](config-route-map)# match ip address prefix-list as-path-prepend-prefix
E_A_BIGIP-13.local[0](config-route-map)# set as-path prepend 988
E_A_BIGIP-13.local[0](config-route-map)#!
E_A_BIGIP-13.local[0](config-route-map)#route-map AS-Path-Prepend-OUT permit 200
E_A_BIGIP-13.local[0](config-route-map)#router bgp 65202
E_A_BIGIP-13.local[0](config-router)#nei 10.2.20.4 route-map AS-Path-Prepend-OUT out
E_A_BIGIP-13.local[0]#clear ip bgp *
E_A_BIGIP-13: Verify AS-Path-Prepend-OUT has inserted 1 AS Path prepend into the prefix towards CPE @ 10.2.20.4:
E_CPE_A_CSR1k: Verify AS-Path-Prepending inbound on E_CPE_A for 10.99.99.0/24 from E_A_BIGIP:
BGP table version is 56, local router ID is 2.2.2.2
t secondary path,
* 10.99.99.0/24 10.2.20.3 4294967295 0 65202 988 i
E_CPE_A_CSR1k: Verify that E_A_BIGIP is no longer an installed route or preferred in BGP RIB for 10.99.99.0/24 on E_CPE_A. You will Note that the next hop for 10.99.99.0/24 is E_B_BIGIP @ 10.2.30.3 and not E_A_BIGIP @ 10.2.20.3.
B 1.1.1.1 [20/4294967294] via 172.16.6.3, 1d01h
B 1.1.1.2 [20/4294967294] via 172.16.6.3, 1d01h
B 3.3.3.3 [20/4294967294] via 10.2.30.3, 00:05:07
[20/4294967294] via 10.2.20.3, 00:05:07
B 10.99.99.0/24 [20/4294967294] via 10.2.30.3, 00:05:11
B 99.99.99.0 [20/4294967294] via 172.16.6.3, 1d01h
B 172.16.1.0/24 [20/4294967294] via 172.16.6.3, 1d01h
B 172.16.2.0/24 [20/4294967294] via 172.16.6.3, 1d01h
B 172.16.99.0/24 [20/0] via 172.16.6.3, 1d01h
csr1000v-E_CPE_A>
Note
Congratulations! E_A_BIGIP has successfully been placed in maintenance mode within the East DC and is no longer taking any traffic. This was achieved by inserting the additional AS Path prepend in the previous step eliminating this as a candidate for BGP multipath selection on E_CPE_A. Let’s continue with additional validation.
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is now installing specific 10.99.99.0/24 from E_B_BIGIP using specific ip route command. Notice the next hop of E_B_BIGIP @ 10.2.30.3:
Tag 65203, type external
Last update from 10.2.30.3 00:00:24 ago
* 10.2.30.3, from 10.2.30.3, 00:00:24 ago
AS Hops 1
Route tag 65203
MPLS label: none
E_CPE_A_CSR1k: Verify that E_CPE_A_CSR1k is now installing specific 10.99.99.0/24 from E_B_BIGIP using specific ip bgp command. Notice the best path is via E_B_BIGIP @ 10.2.30.3 due to AS Path length:
csr1000v-E_CPE_A>show ip bgp vpnv4 vrf internet 10.99.99.0
BGP routing table entry for 65201:1000:10.99.99.0/24, version 53
BGP Bestpath: deterministic-med: aigp-ignore: med
Paths: (2 available, best #1, table internet)
Multipath: eiBGP
3 4
Refresh Epoch 1
65203
10.2.30.3 (via vrf internet) from 10.2.30.3 (10.2.50.3)
Origin IGP, metric 4294967295, localpref 100, valid, external, best
Extended Community: RT:65201:1000
Refresh Epoch 1
65202 988
10.2.20.3 (via vrf internet) from 10.2.20.3 (10.2.40.3)
csr1000v-SP_C: Verify path via Virtual Server 10.99.99.102 is still up via East DC @ E_B_BIGIP now that E_A_BIGIP is in maintenance mode within East DC:
1 172.16.99.4 [AS 65001] 7 msec 7 msec 8 msec
2 172.16.6.4 [AS 65002] 12 msec 14 msec 14 msec
3 10.99.99.102 [AS 988] 18 msec 12 msec 13 msec
csr1000v-SP_C>
Reminder: You can telnet to csr1000v-SP_C from the jumpbox @ 192.168.1.15 with root/default user/pass:
Jumpbox: Verify curl to Virtual Server 10.99.99.102 is still up via East DC @ E_B_BIGIP:
Jumpbox: Verify traceroute to Virtual Server 10.99.99.102 is still up via East DC @ E_B_BIGIP:
1 192.168.1.15 (192.168.1.15) 13.403 ms 13.047 ms 12.418 ms
2 172.16.99.4 (172.16.99.4) 12.830 ms 12.649 ms 12.351 ms
3 172.16.6.4 (172.16.6.4) 31.121 ms 44.958 ms 44.866 ms
4 10.99.99.102 (10.99.99.102) 44.458 ms 45.634 ms 60.454 ms
root@jumphost:~#
Note
Now that E_A_BIGIP is in maintenance mode we only have E_B_BIGIP taking all the traffic within the East DC for Virtual Servers on 10.99.99.0/24 via SP_C.
Let's also match AS Path Prepending on E_B_BIGIP such that both East BIG IP's have been added to maintenance mode and are no longer taking any traffic via SP_C.
This is because the AS Path will be longer via East DC as compared to West DC after we make the next set of changes.
Create AS-Path-Prepend-OUT route-map on E_B_BIGIP for 10.99.99.0/24 to insert 1 AS Path prepend into the prefix:¶
E_B_BIGIP-13: Create AS-Path-Prepend-OUT route-map on E_B_BIGIP for 10.99.99.0/24 to insert 1 AS Path prepend into the prefix:
E_B_BIGIP-13.local[0](config)#ip prefix-list as-path-prepend-prefix seq 10 permit 10.99.99.0/24
E_B_BIGIP-13.local[0](config)#route-map AS-Path-Prepend-OUT permit 100
E_B_BIGIP-13.local[0](config-route-map)# match ip address prefix-list as-path-prepend-prefix
E_B_BIGIP-13.local[0](config-route-map)# set as-path prepend 988
E_B_BIGIP-13.local[0](config-route-map)#route-map AS-Path-Prepend-OUT permit 200
E_B_BIGIP-13.local[0](config-route-map)#router bgp 65203
E_B_BIGIP-13.local[0](config-router)#neighbor 10.2.30.4 route-map AS-Path-Prepend-OUT out
E_B_BIGIP-13.local[0]#clear ip bgp *
E_B_BIGIP-13: Verify AS-Path-Prepend-OUT has inserted 1 AS Path prepend into the prefix towards CPE @ 10.2.30.4:
E_CPE_A_CSR1k: Verify AS-Path-Prepending inbound on E_CPE_A for 10.99.99.0/24 from E_B_BIGIP.
BGP table version is 71, local router ID is 2.2.2.2
t secondary path,
*m 10.99.99.0/24 10.2.30.3 4294967295 0 65203 988 i
Note
You will also notice the ‘m’ notation has been restored above. This means the prefixes are selected for multipath since we have equalized the previous AS Path prepend configured on E_A_BIGIP.
Let's move along...
E_CPE_A_CSR1k: Verify that both E_A_BIGIP & E_B_BIGIP is now valid again for 10.99.99.0/24 on E_CPE_A. You will Note that the next hop for 10.99.99.0/24 is both E_A_BIGIP @ 10.2.20.3 and E_B_BIGIP @ 10.2.30.3
B 3.3.3.3 [20/4294967294] via 10.2.30.3, 00:08:00
[20/4294967294] via 10.2.20.3, 00:08:00
B 10.99.99.0/24 [20/4294967294] via 10.2.30.3, 00:07:57
[20/4294967294] via 10.2.20.3, 00:07:57
csr1000v-E_CPE_A>
Note
Congratulations! E_B_BIGIP has successfully been placed in maintenance mode within the East DC and is no longer taking any traffic. This was achieved by inserting the additional AS Path prepend in the previous step eliminating this as a candidate for BGP multipath selection on E_CPE_A.
Now the entire East DC is in maintenance mode as both E_A_BIGIP and E_B_BIGIP are no longer taking traffic.
That is, 10.99.99.0/24 is preferred via the West DC from the jumpbox when leveraging SP_C. Let’s continue with additional validation.
E_CPE_A_CSR1k: We can observe that prepending is happening for 10.99.99.0/24 on E_CPE_A for both E_A_BIGIP & E_B_BIGIP:
csr1000v-SP_C: Verify 10.99.99.0/24 is available on SP_C BGP RIB table via East DC. You will notice the best path is via West DC via AS 65101.
csr1000v-SP_C>sh ip bgp 10.99.99.100/24
BGP routing table entry for 10.99.99.0/24, version 25
Paths: (2 available, best #2, table default)
1
Refresh Epoch 1
65002 988 988
Refresh Epoch 1
Origin incomplete, localpref 100, valid, external, atomic-aggregate, best
csr1000v-SP_C: Verify 10.99.99.0/24 is no longer installed on SP_C IP routing table via East DC. You will notice the route installed is via West DC via AS 65001.
csr1000v-SP_C>sh ip route 10.99.99.100
Tag 65001, type external
Last update from 172.16.99.3 00:07:29 ago
* 172.16.99.3, from 172.16.99.3, 00:07:29 ago
AS Hops 2
Route tag 65001
MPLS label: none
Note
This prefix is no longer installed in the routing table via East DC because the AS Path length is larger than that of West DC. At this point traffic is now via West DC for 10.99.99.0/24 from SP_C point-of-view.
csr1000v-SP_C: Verify path via Virtual Server 10.99.99.101 is now via West DC - AS 65101. Note that below output may not be an exact match as this can be via either 172.16.1.4 or 172.16.2.4 leveraging AS 65101 via West_CPE_A or West_CPE_B.
csr1000v-SP_C>traceroute 10.99.99.101
Tracing the route to 10.99.99.101
1 172.16.99.3 [AS 65001] 8 msec 8 msec 7 msec
2 172.16.1.4 [AS 65001] 11 msec 8 msec 10 msec
3 10.99.99.101 [AS 65101] 14 msec 13 msec 15 msec
csr1000v-SP_C>
Jumpbox: Verify curl to Virtual Server 10.99.99.101 is up via West DC:
Jumpbox: Verify traceroute to Virtual Server 10.99.99.101 is West DC. Note that below output may not be an exact match as this can be via either 172.16.1.4 or 172.16.2.4 leveraging AS 65101 via West_CPE_A or West_CPE_B.
root@jumphost:~# traceroute 10.99.99.101
traceroute to 10.99.99.101 (10.99.99.101), 30 hops max, 60 byte packets
1 192.168.1.15 (192.168.1.15) 2.504 ms 15.470 ms 15.277 ms
2 172.16.99.3 (172.16.99.3) 18.709 ms 19.369 ms 19.762 ms
3 172.16.2.4 (172.16.2.4) 25.569 ms 28.738 ms 44.922 ms
4 10.99.99.101 (10.99.99.101) 44.591 ms 47.980 ms 51.598 ms
root@jumphost:~#
Anycast DC Failover section - Swing Traffic back to East DC by adding 2 x /25 specific routes which comprise of the overall 10.99.99.0 /24¶
Note
In previous section we verified that 10.99.99.0/24 is only installed in the IP Routing table of SP_C via West DC. However, East DC is available as backup path in BGP RIB.
In this section we will swing traffic back to East DC by utilizing 2 x /25's.
E_A_BIGIP-13: Configure BGP on E_A_BIGIP-13 to originate 10.99.99.0 /25 and 10.99.99.128 /25:
E_A_BIGIP-13.local[0](config-router)#network 10.99.99.0/25
E_A_BIGIP-13.local[0](config-router)#network 10.99.99.128/25
E_A_BIGIP-13.local[0](config)#end
E_A_BIGIP-13: Verify 10.99.99.0/24, 10.99.99.0/25, and 10.99.99.128/25 are advertised via E_A_BIGIP to E_CPE_A @ 10.2.20.4:
E_A_BIGIP-13.local[0]#sh ip bgp nei 10.2.20.4 ad
BGP table version is 2, local router ID is 10.2.40.3
*> 3.3.3.3/32 10.2.20.3 0 65205 i
*> 10.3.99.0/24 10.2.20.3 0 65205 i
*> 10.99.99.0/24 10.2.20.3 100 32768 988 i
*> 10.99.99.0/25 10.2.20.3 100 32768 i
*> 10.99.99.128/25 10.2.20.3 100 32768 i
Total number of prefixes 5
csr1000v-SP_C: Verify 10.99.99.0/25 is available on SP_C BGP RIB table via East DC leveraging 10.99.99.0 /25. You will notice the best path is via East DC via AS 65002 988.
Reminder: You can telnet to csr1000v-SP_C from the jumpbox @ 192.168.1.15 with root/default user/pass.
csr1000v-SP_C>sh ip bgp 10.99.99.102
BGP routing table entry for 10.99.99.0/25, version 30
1
Refresh Epoch 1
65001 65002 988
Refresh Epoch 1
65002 988
csr1000v-SP_C: Let's also verify 10.99.99.0/25
csr1000v-SP_C>sh ip bgp 10.99.99.0/25
BGP routing table entry for 10.99.99.0/25, version 26
1
Refresh Epoch 1
65001 65002 988
Refresh Epoch 1
65002 988
csr1000v-SP_C: Verify 10.99.99.102 is installed on SP_C IP routing table via East DC leveraging 10.99.99.0/25. You will notice the route installed is via East DC via AS 65002.
csr1000v-SP_C>sh ip route 10.99.99.102
Routing entry for 10.99.99.0/25
Last update from 172.16.99.4 00:03:10 ago
* 172.16.99.4, from 172.16.99.4, 00:03:10 ago
AS Hops 2
Route tag 65002
MPLS label: none
Note
You will observe that the IP Routing table of SP_C will prefer the path via East DC for the 10.99.99.102 Virtual Server due longest match of 10.99.99.0/25 even though 10.99.99.0/24 is via West DC.
We can expect the same behavior with 10.99.99.128 /25. Let’s validate.
csr1000v-SP_C: Verify 10.99.99.128 /25 is available on SP_C IP BGP RIB table via East DC. You will notice the best path is via East DC via AS 65002 988.
csr1000v-SP_C>sh ip bgp 10.99.99.128/25
BGP routing table entry for 10.99.99.128/25, version 39
1
Refresh Epoch 1
65001 65002 988
Refresh Epoch 1
65002 988
csr1000v-SP_C: Verify 10.99.99.128 /25 is installed on SP_C IP routing table via East DC leveraging 10.99.99.128 /25. You will notice the route installed is via East DC via AS 65002.
csr1000v-SP_C>sh ip route 10.99.99.128 255.255.255.128
Routing entry for 10.99.99.128/25
Last update from 172.16.99.4 00:03:16 ago
* 172.16.99.4, from 172.16.99.4, 00:03:16 ago
AS Hops 2
Route tag 65002
MPLS label: none
Note
What observations are made with 10.99.99.0/24? You will notice this remains the same with West DC preferred via AS Path length for 10.99.99.0/24.
csr1000v-SP_C: Verify 10.99.99.0 /24 is available on SP_C BGP RIB table via West DC. You will notice the best path is via West DC via AS 65101.
1
Refresh Epoch 1
65002 988 988
Refresh Epoch 1
csr1000v-SP_C: Verify 10.99.99.0 /24 is available on SP_C IP routing table via West DC. You will notice the best path is via West DC via AS 65001.
Last update from 172.16.99.3 01:00:50 ago
* 172.16.99.3, from 172.16.99.3, 01:00:50 ago
AS Hops 2
Route tag 65001
MPLS label: none
csr1000v-SP_C: Verify path via Virtual Server 10.99.99.102 is now via East DC due to the /25's being originated from East DC via E_A_BIGIP-13 .
1 172.16.99.4 [AS 65001] 7 msec 6 msec 8 msec
2 172.16.6.4 [AS 65002] 9 msec 12 msec 10 msec
3 10.99.99.102 [AS 988] 17 msec 21 msec 16 msec
csr1000v-SP_C>
Jumpbox: Verify curl to Virtual Server 10.99.99.102 is up via East DC:
Jumpbox: Verify traceroute to Virtual Server 10.99.99.102 is East DC.
1 192.168.1.15 (192.168.1.15) 14.200 ms 14.073 ms 13.654 ms
2 172.16.99.4 (172.16.99.4) 21.305 ms 27.179 ms 27.071 ms
3 172.16.6.4 (172.16.6.4) 26.755 ms 26.447 ms 26.119 ms
4 10.99.99.102 (10.99.99.102) 36.549 ms 48.875 ms 48.795 ms
root@jumphost:~#
Note
Congratulations! You have successfully swing traffic back to the East DC even though 10.99.99.0/24 is currently preferred via West DC from SP_C. This was accomplished by introducing specific /25’s from the East DC via E_A_BIGIP-13.
Let’s finish this off as you are in the home stretch! We will finish the East DC by originating the same /25’s on E_B_BIGIP-13 for consistency with E_A_BIGIP-13.
Re-introduce E_B_BIGIP-13 in the East DC via the /25's:¶
In this section we will finish the configuration on the East DC to originate the 2 x /25's on E_B_BIGIP-13. This will match the origination of 2 x 25’s previously completed on E_A_BIGIP-13.
E_B_BIGIP-13: Configure BGP on E_B_BIGIP-13 to originate 10.99.99.0 /25 and 10.99.99.128 /25:
E_B_BIGIP-13.local[0]>enE_B_BIGIP-13.local[0]#conf t
E_B_BIGIP-13.local[0](config-router)#network 10.99.99.0/25
E_B_BIGIP-13.local[0](config-router)#network 10.99.99.128/25
E_B_BIGIP-13.local[0](config)#end
E_B_BIGIP-13: Verify 10.99.99.0/24, 10.99.99.0/25, and 10.99.99.128/25 are advertised via E_B_BIGIP to E_CPE_A @ 10.2.30.4:
E_B_BIGIP-13.local[0]#sh ip bgp nei 10.2.30.4 advertised-routes
BGP table version is 9, local router ID is 10.2.50.3
*> 3.3.3.3/32 10.2.30.3 0 65205 i
*> 10.3.99.0/24 10.2.30.3 0 65205 i
*> 10.99.99.0/24 10.2.30.3 100 32768 988 i
*> 10.99.99.0/25 10.2.30.3 100 32768 i
*> 10.99.99.128/25 10.2.30.3 100 32768 i
E_CPE_A_CSR1k: Verify that 10.99.99.0/24, 10.99.99.0/24, and 10.99.99.128/25 are learned via the routing table on E_CPE_A from both E_A_BIGIP @ 10.2.20.3 and E_B_BIGIP @ 10.2.30.3
B 1.1.1.1 [20/4294967294] via 172.16.6.3, 1d02h
B 1.1.1.2 [20/4294967294] via 172.16.6.3, 1d02h
B 3.3.3.3 [20/4294967294] via 10.2.30.3, 00:04:59
[20/4294967294] via 10.2.20.3, 00:04:59
10.0.0.0/8 is variably subnetted, 7 subnets, 3 masks
B 10.99.99.0/24 [20/4294967294] via 10.2.30.3, 00:05:20
[20/4294967294] via 10.2.20.3, 00:05:20
B 10.99.99.0/25 [20/4294967294] via 10.2.30.3, 00:05:28
[20/4294967294] via 10.2.20.3, 00:05:28
B 10.99.99.128/25 [20/4294967294] via 10.2.30.3, 00:05:28
B 99.99.99.0 [20/4294967294] via 172.16.6.3, 1d03h
B 172.16.1.0/24 [20/4294967294] via 172.16.6.3, 1d02h
B 172.16.2.0/24 [20/4294967294] via 172.16.6.3, 1d02h
B 172.16.99.0/24 [20/0] via 172.16.6.3, 1d03h
csr1000v-E_CPE_A>
E_CPE_A_CSR1k: As an example, let’s take a closer look the bgp table for 10.99.99.128/25 on E_CPE_A:
csr1000v-E_CPE_A>sh ip bgp vpnv4 vrf internet 10.99.99.128/25
BGP routing table entry for 65201:1000:10.99.99.128/25, version 98
Multipath: eiBGP
3 4
Refresh Epoch 1
65202
Origin IGP, metric 4294967295, localpref 100, valid, external, multipath, best
Refresh Epoch 1
65203
Origin IGP, metric 4294967295, localpref 100, valid, external, multipath(oldest)
csr1000v-SP_C: Verify nothing changed w.r.t. 10.99.99.0/25 and 10.99.99.128/25 and are still in the IP Routing table of SP_C via East DC after adding the /25's on E_B_BIGIP-13.
First let’s take a look at the BGP table and confirm nothing changed since we previously added the 2 x /25’s on E_A_BIGIP-13 and now completed E_B_BIGIP-13.
First will be 10.99.99.0 /25:
csr1000v-SP_C>sh ip bgp 10.99.99.0 255.255.255.128
BGP routing table entry for 10.99.99.0/25, version 38
1
Refresh Epoch 1
65001 65002 988
Refresh Epoch 1
65002 988
Second will be 10.99.99.128 /25:
csr1000v-SP_C>sh ip bgp 10.99.99.128 255.255.255.128
1
Refresh Epoch 1
65001 65002 988
Refresh Epoch 1
65002 988
Last will be 10.99.99.0 /24:
csr1000v-SP_C>sh ip bgp 10.99.99.0 255.255.255.0
1
Refresh Epoch 1
65002 988 988
Refresh Epoch 1
Note
You will also observe that the IP Routing table on SP_C will still prefer West DC for the 10.99.99.0/24 due to previous AS Path Prepending exercise inserted from the East DC towards SP.
csr1000v-SP_C: Now let’s take a look at the ip routing table and confirm nothing has changed since we previously added the 2 x /25’s on E_A_BIGIP-13 and now completed E_B_BIGIP-13.
csr1000v-SP_C>sh ip route 10.99.99.0 255.255.255.128
Last update from 172.16.99.4 00:19:27 ago
* 172.16.99.4, from 172.16.99.4, 00:19:27 ago
AS Hops 2
Route tag 65002
MPLS label: none
Last update from 172.16.99.4 00:19:34 ago
* 172.16.99.4, from 172.16.99.4, 00:19:34 ago
AS Hops 2
Route tag 65002
MPLS label: none
AS Hops 2
Route tag 65001
MPLS label: none
csr1000v-SP_C: Verify path via Virtual Server 10.99.99.102 is still via East DC with introduction of adding the /25's from East DC via both E_A_BIGIP-13 & E_B_BIGIP-13 .
2 172.16.6.4 [AS 65002] 23 msec 11 msec 11 msec
3 10.99.99.102 [AS 988] 14 msec 16 msec 14 msec
csr1000v-SP_C>
1 192.168.1.15 (192.168.1.15) 23.599 ms 21.587 ms 20.725 ms
2 172.16.99.4 (172.16.99.4) 25.015 ms 24.031 ms 23.148 ms
3 172.16.6.4 (172.16.6.4) 34.033 ms 33.082 ms 38.138 ms
4 10.99.99.102 (10.99.99.102) 37.173 ms 36.389 ms 53.688 ms
Note
Congratulations! This section is now complete and everything checks out as expected. We are now going to move on to the final step and validate with a Virtual Server on the upper /25 – 10.99.99.128 /25.
Create an application configuration for a virtual server and a pool member on E_A_BIGIP-13 and E_A_BIGIP-13 to validate reachability via 10.99.99.128/25:¶
Create the following virtual server and pool member on both E_A_BIGIP-13 and E_B_BIGIP-13
root@E_A_BIGIP-13:Active:Standalone] config # tmsh show ltm virtual vip3
Ltm::Virtual Server: vip3
Status
State : enabled
CMP : enabled
CMP Mode : all-cpus
Destination : 10.99.99.129:80
root@E_B_BIGIP-13:Active:Standalone] config # tmsh show ltm virtual vip3
Status
State : enabled
CMP : enabled
CMP Mode : all-cpus
Verify path via Virtual Server 10.99.99.129 which falls on 10.99.99.128/25 is via East DC with introduction of adding the /25's from East DC.
csr1000v-SP_C: Verify path via Virtual Server 10.99.99.129 which falls on 10.99.99.128/25 is via East DC with introduction of adding the /25's from East DC. You can validate via traceroute to 10.99.99.129 on SP_C:
csr1000v-SP_C: You can validate via show ip route for 10.99.99.129 on SP_C:
csr1000v-SP_C>sh ip route 10.99.99.129
Last update from 172.16.99.4 00:24:58 ago
* 172.16.99.4, from 172.16.99.4, 00:24:58 ago
AS Hops 2
Route tag 65002
MPLS label: none
csr1000v-SP_C>
Jumpbox: Verify curl to Virtual Server 10.99.99.129 is up via East DC:
Jumpbox: Verify traceroute to Virtual Server 10.99.99.129 is East DC.
root@jumphost:~# traceroute 10.99.99.129
traceroute to 10.99.99.129 (10.99.99.129), 30 hops max, 60 byte packets
1 192.168.1.15 (192.168.1.15) 2.569 ms 9.153 ms 9.097 ms
2 172.16.99.4 (172.16.99.4) 23.348 ms 22.639 ms 22.585 ms
3 172.16.6.4 (172.16.6.4) 25.018 ms 24.391 ms 23.766 ms
4 10.99.99.129 (10.99.99.129) 30.824 ms 30.220 ms 39.918 ms
root@jumphost:~#
Note
Congratulations! You have successfully completed lab 2.